AC Entrance Requirements

The power strips provided with the hardware use a detachable inlet cord set that mates to an IEC 320 - C20 receptacle on the power strip. Unisys provides three types of power cords; select the appropriate power cord based on your location and provide the applicable mating receptacle. In addition to power cords available from Unisys, you can choose to use cord sets that meet local standards and codes with localized plugs that are not supplied by Unisys.

Each power cord must be protected by circuit breakers with the applicable rating.

Power cords are a maximum of 3 m (10 ft) in length. Receptacles should be located within 2 m (6.6 ft) of the cabinet to allow adequate length for routing power cords within the cabinet while avoiding undue stress on the cords.

The AC entrance requirements, available power cords, and mating receptacle requirements are listed in AC Entrance Requirements and Available Power Cords and Mating Receptacle Requirements.

Table 2. AC Entrance Requirements

Locality

Frequency

Voltage

Number of AC Entries Required per Cabinet

Input Source AC Circuit Rating

Power Strip Output Load Rating

US, Canada

50/60 Hz

200 – 240 V

1 phase

4 or 6

20 A

16 A

International

50/60 Hz

200 – 240 V

1 phase

4 or 6

16 A

16 A


Table 3. Available Power Cords and Mating Receptacle Requirements

Locality

Power Cord Type

Connector Description

Mating Receptacle Face View (Customer-Supplied)

US, Canada

LC1-M

NEMA L6-20R (20 A , 208 V, 2 power, 3 wires)

International

LC1-Q

IEC 60309 316-R6 (16 A, 200 to 250 V, 2 power, 3 wires)

Note: Alternate receptacle description is IEC 60309 16 A.

LC1-UVH

No Plug (16 A, 200 to 240 V, Live: Brown, Neutral: Blue, Ground: Green/Yellow)


For a large fabric environment that includes four or more 4-socket enterprise partition platforms in the same cabinet, higher capacity power strips (a restricted option) may be required. The AC entrance requirements, available power cords, and mating receptacle requirements for higher capacity power strips are listed in AC Entrance Requirements of Higher Capacity Power Strips and Available Power Cords and Mating Receptacle Requirements of Higher Capacity Power Strips.

Table 4. AC Entrance Requirements of Higher Capacity Power Strips

Locality

Frequency

Voltage

Number of AC Entries Required per Cabinet

Input Source AC Circuit Rating

Power Strip Output Load Rating

US, Canada

50/60 Hz

200 – 240 V

1 phase

4 or 6

30 A

24 A

International

50/60 Hz

200 – 240 V

1 phase

4 or 6

30 A

24 A


Table 5. Available Power Cords and Mating Receptacle Requirements of Higher Capacity Power Strips

Locality

Power Cord Type

Connector Description

Mating Receptacle Face View (Customer-Supplied)

US, Canada

LC1-S with 8 outlet power strip

NEMA L6-30R (30 A, 208 V, 2 power, 3 wires)

International

LC1-R with 8 outlet power strip

IEC 60309-32 A (32 A, 200 to 250 V, 2 power, 3 wires)

Note: Alternate receptacle description is IEC 60309 32 A.

LC1-UVH with 8 outlet power strip

No Plug (32 A, 200 to 240 V, Live: Brown, Neutral: Blue, Ground: Green/Yellow)